Do the same exercise as above with the replacement of the earlier transformer by a 40,000-200 V step-down transformer (Neglect, as before, leakage losses though this may not be a good assumption any longer because of the very high voltage transmission involved). Hence, explain why high voltage transmission is preferred?

Solution

Given, 

Primary voltage, V = 40000 V 

Now, using the formula of power we get,
                        P = VP I
      40,000 × IP = 800 × 1000 
                       IP = 20 A
which, is the rms value of current or current in the primary coil.

(a) Line power loss = Iv2 R
                            = (20)2 × 15
                            = 6000 W
                            = 6 kW

(b) Power supplied by the plant = 800 + 6
                                             = 806 kW 

(c) Voltage drop on the line = IP × R
                                       = 20 × 15
                                       = 300 V 

 Voltage output of the step-up transformer at the plant = 40000 + 300= 40300 V 

∴ The step-up transformer at the plant need a voltage of 440 V – 40300 V.

Power loss at lower voltage = 6001400×100 = 43% 

Power loss at higher voltage = 6800×100 = 0.74% 
Hence, it is evident that power loss is minimal when voltage is high. Therefore, high voltage transmission is produced.